Dear easy poweful users; :D
Hello, today I have one question.
According to the Technical data, easy 512-...-R's minimun current
is 500mA (12V).
But if I want to use "Relay type" (not Transistor type) in the control circuit,
It is too high.
Accutually is it really 500mA ?
I hope it can be used around 10mA.
Sincerely
Michiyo Fujisaki
???
-
Hi Fujisaki,
There is no problem if you use relay output. This is know as dry contact, its means that not matter what is connected (DC, AC, low or high current) will complete the circuit. The relay type has a maximum capacity of 8A if you are not above this you are ok. ;D