Hello!
Is it possible to automatically put PLC (easy 412 AC-RC) into run mode after power is turned on (for example after power lost)?
Thanks
-
Push Alt + DEL together
Roll with Cursot Button to "System"
Push OK
Set the Ticker by "Run Mode"
That's it
Regards
Hermann
-
Thank you very much.
I have managed to solved my problem.
The only problem was that "my logic was inverted".
My Easy 412 doesn't show selected settings by placing check mark next to menu item!
I saw text "Mode: run" <-- and I was thinking it is already in run mode --> so I exit the system menu.
All I had to do was to push the OK button to actually set the run mode.
So if you see "Mode: run", PLC is currently in STOP mode (and vice versa).
Thanks again,
Regards
Damjan
-
Hi Damjan
I remember. By older version of Eras this Mode was Invers. Not only you, many other User had the problem you've told about. Later then Moeller realised it and changet the function. I'm happy I could help to change your Easy to Auto-Start Mode :D
Regards
Hermann