easy-forum
Deutsch - Hardware => MFD-Titan® => Thema gestartet von: mebots am September 12, 2008, 11:01:11 Vormittag
-
Hallo,
have following problem, have a AR01CY Block
I1 = 54
I2 = 3600
QV = MW01
Mode = DIV
Is there a possible way to deal with 0,01 values
Because this gives 0.
With regards,
Martijn
-
Hello mebots
the representation of decimal figures in the Easy800 not possible.
Regards Jan
-
Hello Mebots,
do you only need the value for calculating or do you want to display it?
If you need it only for calculation you can multiply the value 54 (I1) by 1000 for e.g.
so you have 54000/3600 = 15.
In that case you have to keep in mind that operation.....don´t forget to divide your result by 1000 to get the right value
Thats the same way I do when I handle with values like 0,00578 .....I multiply them by 1000000 so I can calculate with them
regards
jan
-
Hello Jan,
Thanks for the reply, I was thinking the same :)
But want also display it, can it be done ?
Have made a mistake it's also a 120 L/h pump.
So it will be (120 x 1000) / 3600 = 33,3 will be 33 have only a mistake from 0,3 / 1000 right ?
thanx
-
right :)