Hi, firstly I'm using a 821, pt12 b with CPU and mfd 80 with CPU.
Mfd is net 1, pt is net 2 and 821 is net 3.
My program is installed on the mfd CPU.
I'm using 2 x pt 100's
the help file says the plc automatically assigns IA1 to the input one on the pt 12 and IA2 to input 2 on the pt 12.
My mfd is set to display the value of IA1 as a word and IA2 as a word.
My program has 2 comparator blocks using IA1 and 2 against a constant value.
When I connect my pt100 as per drawings with link I don't get any values.
Is there more options to configure this. Do I set the inputs as IA or MD ?
-
Dear craigb.
As far as I understood you only have one program in Net-Id1 and you like to use
the Net-Id's 2 and 3 as remote - I/O stations without program.
This works fine as long as your inputs are of digital type only. For analogue inputs
like your PT100's this method is not usable.
You need a small program at Net-ID2 to send the values by PT-function and at Net-ID1
you need a sequence to receive the values with GT-function. Therefore you also have to
change the type of sending/receiving digital informations to RN- and SN-function.
At the moment you are displaying the analogue values of the local inputs (IA1 of Net-Id1),
which is 0.
Regards
Maikky
-
Thankyou, that makes sense
later on I will have a go at the program on net 2 (pt 12 b)
I assumed automatically that net Id 1 (mfd Titan display) woudd automatically use the IA's of another station as net 1 doesn't have any inputs.
Is there any examples of programs that use this function to send analogue inputs over net? I assume it's just a case of sending a word fron net 2 to net 1?
-
Dear craigb.
Attached please find a similar example.
Regards
Maikky
-
Thank you for that. I managed to write the program before I was able to look at the example, It wasnt as hard as I expected.
I did have a problem initially of ID2 sending one value to ID1. Where you used Marker 1, I used a flashing timer with 20ms delays.
The hardest part was trying to work out the scaling. Is there a formular for this ?
Will I also have to put ID 17 - 23 in ID 2 (Pt12 B)
While Im on this subject, every time I open my program I get a message popping up that says your program contains one or several unsupported expansion devices, they will be removed from the configuration.
I press ok, but nothing changes and I get this every time.
Doesnt seem to cause a problem but indicates something is wrong.
-
Dear craigb.
Maybe it's useful to upload your program "as is" so others can have a look whether there
is something wrong.
Regards
Maikky
-
This is the program on my laptop I have now. My revised version that I done today with the Get and Put's is on my work laptop. This version is more or less identicle.
-
Just to add,
The 'R' inputs were only used for simulation purposes as at the time of writing I never had the PLC with me.
I used 'R' as there was no way to simulate the NET ID3 inputs.
-
Dear craigb.
To delete the warning message of unsupported devices you have to re-configure your modules.
- select the first module at project view
- right click, a window pops up, select exchange ?? (see attachment 1, I am using the German
version and do not know the English menu item)
- the module changes colour (see attachment 2)
- pick the same module and place it
- repeat for the remaining modules
Now the message does not appear any more.
Regards
Maikky
-
Dear craigb.
You are able to simulate the received bits from Net-Id3.
During simulation select the display view - RN Receive Bit - NET-ID3 and mark the proper
bit (for example RN1 in attached screen shot).
Regards
Maikky
-
Thankyou for your help once again, It has been much appreciated...
Another problem ::)
Ive atached the latest version of the program, It will not let me assign any inputs or outputs to NET 2. Net 2 being the Tp12 b module withi has digital inputs.
If you press simulate you will see the error pop up.
-
Dear craigb.
The problem is related to my earlier answer. Net-Id2 has to contain a program, because
you are using analogue value. It is not a remote-I/O module.
Therefore you also have to change the type of sending/receiving digital informations to
RN- and SN-function.
Attached please find the modified program.
Regards
Maikky