not sure we can do this with an easy e4, we have 4 borehole pumps which all have a water meter pulsed output. we need to count the cube of each pump for each month from march to october and retain the monthly totals for each pump until the following year when they then need to be reset. unless anybody knows of another way i tried it but need 36counters one for each pump each month. Anybody got any ideas. I do my programming in LD. Cheers
-
What is the maximum pulse rate when the pump is running?
-
1 pulse every second maximum
-
You can use normal counters to count the pulses and make the counters remanent. Using the RTC you can calculate the difference at the end of the month and write the result into a remanent DW or DW shift register.
-
this is an example in ST
RC01 (
EN := true,
DT => ,
E1 => ,
YY => ,
MM => ,
DD => ,
WD => ,
HR => ,
MN => ,
SC => );
//Trigger, if the next month
M02:= (RC01MM<>MB70) and M01;
MB70:= RC01MM;
//Pump 1
C01 (
EN := true,
C_ := I01,
D_ := ,
SE := ,
RE := ,
SH := ,
SL := ,
SV := ,
OF => ,
FB => ,
CY => ,
ZE => ,
QV => );
//in 1st cycle of the new month calculate the difference to the last
CASE MB70 OF
1: IF M02 THEN MD51:= C01QV - MD50; END_IF;
2: IF M02 THEN MD40:= C01QV - MD51; END_IF;
3: IF M02 THEN MD41:= C01QV - MD40; END_IF;
4: IF M02 THEN MD42:= C01QV - MD41; END_IF;
5: IF M02 THEN MD43:= C01QV - MD42; END_IF;
6: IF M02 THEN MD44:= C01QV - MD43; END_IF;
7: IF M02 THEN MD45:= C01QV - MD44; END_IF;
8: IF M02 THEN MD46:= C01QV - MD45; END_IF;
9: IF M02 THEN MD47:= C01QV - MD46; END_IF;
10: IF M02 THEN MD48:= C01QV - MD47; END_IF;
11: IF M02 THEN MD49:= C01QV - MD47; END_IF;
12: IF M02 THEN MD50:= C01QV - MD47; END_IF;
ELSE
;
END_CASE;
//Pump 2
C02 (
EN := true,
C_ := I02,
D_ := ,
SE := ,
RE := ,
SH := ,
SL := ,
SV := ,
OF => ,
FB => ,
CY => ,
ZE => ,
QV => );
//in 1st cycle of the new month calculate the difference to the last
CASE MB70 OF
1: IF M02 THEN MD63:= C01QV - MD62; END_IF;
2: IF M02 THEN MD52:= C01QV - MD63; END_IF;
3: IF M02 THEN MD53:= C01QV - MD52; END_IF;
4: IF M02 THEN MD54:= C01QV - MD53; END_IF;
5: IF M02 THEN MD55:= C01QV - MD54; END_IF;
6: IF M02 THEN MD56:= C01QV - MD55; END_IF;
7: IF M02 THEN MD57:= C01QV - MD56; END_IF;
8: IF M02 THEN MD58:= C01QV - MD57; END_IF;
9: IF M02 THEN MD59:= C01QV - MD58; END_IF;
10: IF M02 THEN MD60:= C01QV - MD59; END_IF;
11: IF M02 THEN MD61:= C01QV - MD60; END_IF;
12: IF M02 THEN MD62:= C01QV - MD61; END_IF;
ELSE
;
END_CASE;
//end of program
M01:= true; //false in 1st cycle
-
You wrote 'we need to count the cube of each pump for each month from march to october'
The other way is with a counter per pump to. Permanent write the actual QV to a DW pointed by month number in a CASE.
8 months for 8 QA's in a UF. It's better you write the ST code, 1 per pump, in a UF and use the UF in your LD Mainprogram.
Reset the counter with the same Trigger:
//Trigger, if the next month
M02:= (RC01MM<>MB70) and M01;
MB70:= RC01MM;
Or positive Trigger coil in LD
Use RC01 and Trigger in the Mainprogram
-
Cheers for that i will give it a try