Titel: mains water valve
Beitrag von: srd am Oktober 02, 2024, 15:51:39 Nachmittag
we have a 4-20ma / 3m transducer i a tank, we have and analogue module on an easy e4what is the best way to open the mains water solenoid valve at 2.2m and close at 2.6m. If somebody has and example in FDB that would be helpful. Cheers
Titel: Antw:mains water valve
Beitrag von: radar17892 am Oktober 02, 2024, 21:07:29 Nachmittag
hello srd, When I get back on
 Weekend I can write you a UF block. Because these are comparisons and calculations, I would write them in ST in the UF.

Thomas
Titel: Antw:mains water valve
Beitrag von: radar17892 am Oktober 06, 2024, 12:51:16 Nachmittag
Hi srd,
here comes the soucecode for you

Zitat
(*
level controller
I01 = EN
IA1 = analog Input 4-20mA
Q1 = open Valve
QA1 = Level in mm *)
// PT1 Filter
FT01 (
   EN := true,
   I1 := IA01,//analog Input 4-20mA
   TG := 30,
   KP := 100,
   CY => ,
   QV => );
//scale Var to mm Level   
//If the sensor works from top to bottom, swap the level values   
LS01 (
   EN := true,
   I1 := FT01QV,
   X1 := 819,   //4mA
   Y1 := 0,//0mm level
   X2 := 4095,   //20mA
   Y2 := 3000,//3000mm level
   QV => QA1); //Leveloutput in mm
//Level controller with fixed setpoints   
IF (LS01QV >= 2600)OR NOT I01 THEN   //close valve, if higher than 2600mm
   Q01:= false;
ELSIF (LS01QV < 2200) and I01 THEN   //open valve, if lower than 22000mm
   Q01:= true;
ELSE   ;
END_IF;

Please also note: what happens if the analog signal fails, will the tank possibly be overfilled?

and the UF to import in your Project

Thomas
Titel: Antw:mains water valve
Beitrag von: srd am Oktober 07, 2024, 12:59:08 Nachmittag
Cheers for that Thomas