motorised valve
« am: Oktober 23, 2026, 09:43:09 Vormittag »
Hi All, i have set up a motorised valve in test running of a pid loop (DC). got it running ok but it runs the reverse of what i require. we have a valve in a ditch chamber when the level rises above our set point we want to open the valve so the level drops to maintain a set level, however on my test rig the valve opens when the water level falls which is the reverse of what we are after. Anybody got any ideas where i have gone wrong.

Offline radar17892

  • Sr. Member
  • ****
  • Beiträge: 921
  • Think easy!
    • mollgruppe
Antw:motorised valve
« Antwort #1 am: Oktober 23, 2026, 11:35:03 Vormittag »
You can negate the feedback in the control loop.