easy-forum
English Support - Software => easySoft => Thema gestartet von: Gayathri L am Januar 27, 2024, 12:26:54 Nachmittag
-
Hi,
I'm working on Eaton EASY-E4-DC-12TC1P and EasySoft 7 V7.4.1.
I have a issue when I'm using LS-Value Scaling component.
Please find the attached pdf of LD program where Network 1 to Network 10 work perfectly fine before adding Network 11. Once Network 11 (LS-Vaue Scale) is added, the Cycle_Started marker is failing to set and is giving unexpected results.
Please help me out with this issue as I'm new to Eaton and EasySoft.
-
Hallo,
Hello,
you use bit flags M 1,2,3,4 ... and in network 11 the MW 1.
These influence each other.
Use a different MW on network 11
See image
du verwendest Bit Merker M 1,2,3,4 ... und in Netzwerk 11 das MW 1.
Das beeinflusst sich gegenseitig.
Verwende in Netzwerk 11 ein anderes MW