English Support - Software => easySoft => Thema gestartet von: Gayathri L am Januar 27, 2024, 12:26:54 Nachmittag

Titel: Value Scaling Issue
Beitrag von: Gayathri L am Januar 27, 2024, 12:26:54 Nachmittag
Hi,

I'm working on Eaton EASY-E4-DC-12TC1P and EasySoft 7 V7.4.1.

I have a issue when I'm using LS-Value Scaling component.
Please find the attached pdf of LD program where Network 1 to Network 10 work perfectly fine before adding Network 11. Once Network 11 (LS-Vaue Scale) is added, the Cycle_Started marker is failing to set and is giving unexpected results.

Please help me out with this issue as I'm new to Eaton and EasySoft.

Titel: Antw:Value Scaling Issue
Beitrag von: Juergen am Januar 27, 2024, 19:58:04 Nachmittag
Hallo,

Hello,

you use bit flags M 1,2,3,4 ... and in network 11 the MW 1.
These influence each other.

Use a different MW on network 11
See image


du verwendest Bit Merker M 1,2,3,4 ... und in Netzwerk 11 das MW 1.
Das beeinflusst sich gegenseitig.

Verwende in Netzwerk 11 ein anderes MW