easy-forum
English Support - Hardware => easyE4 => Thema gestartet von: fentini am Februar 21, 2023, 11:56:36 Vormittag
-
Hello,
I would like to change the time a timer runs according to a digital or analog input that I connect to my Eaton Easy E4.
There is this valve that is being opened by the eaton e4. But sometimes I want the valve to open longer/shorter. I thought I would buy a 0-10 V generator and then connect it to Input 5 of the relais so that I can increase/decrease the voltage on that input. Then on the software I change the I1 of the Timing Relais to "analog inputs/outputs and markers". But that is where I get stuck. Perhaps there are people who can help or maybe there is a topic on this which I have not found?
Thanks in advance.
Chris
-
Hi Chris,
is the LD below, that what you mean?
Note: a time change at the input while the timer is running has no effect. The input is only read at the start of the timer.
Regards Thomas
-
Hi Chris,
is the LD below, that what you mean?
Note: a time change at the input while the timer is running has no effect. The input is only read at the start of the timer.
Regards Thomas
Oh wow, yes, thanks a lot!! You helped me a lot.
Happy with that!!!!!!!!!
Regards Chris