Hi, I'm straggling with Modbus RTU. I have set all communication data between Master and slave but I don't understand a logic of writing of a single coil and MU acyclic request module. How I need to write a program.
I'm asking Eaton or other forum expert to provide me an example.
Thank you in advance Ales
-
hallo,
please upload the project
-
hallo,
please upload the project
Hi w.sprungmann,
please find attached the project
-
The Modbus register table is required for correct addressing.
See example image below.
-
Hi radar17892,
I have try it but doesn't work
-
Hello Ales,
I've taken a look at your project and I think you don't need a MU block. You're already writing Q33 cyclically (100ms) to Slave 1.
It makes no sense to use an acyclic MU block in the program if it is triggered cyclically.
Can you post a picture of the slave Modbus registers?
Please highlight the variables you want to communicate with slave 1.
Thomas
-
Hello all!
I did not have a look onto the entire program...
Only one question: Are you sure you can write a coil?
Not all systems allow to write coils for security reasons. Because if you do so, the automation program loses control on coils.
Just an idea.
Geetz konni
-
Hi radar17892,
please find attached the pictures.
If I not use MU block how can I define which MW will be my used in my project?
Ales
Hello Ales,
I've taken a look at your project and I think you don't need a MU block. You're already writing Q33 cyclically (100ms) to Slave 1.
It makes no sense to use an acyclic MU block in the program if it is triggered cyclically.
Can you post a picture of the slave Modbus registers?
Please highlight the variables you want to communicate with slave 1.
Thomas
-
Hi Konni66,
Yes, I'm sure, I have a slave with 32 relays.
https://www.waveshare.com/Modbus-RTU-Relay-32CH.htm
BR.,
Ales
Hello all!
I did not have a look onto the entire program...
Only one question: Are you sure you can write a coil?
Not all systems allow to write coils for security reasons. Because if you do so, the automation program loses control on coils.
Just an idea.
Geetz konni
-
This is what I needed:
https://www.waveshare.com/wiki/Modbus_RTU_Relay_32CH (https://www.waveshare.com/wiki/Modbus_RTU_Relay_32CH)
Register Address Introduction and Modbus RTU Command Introduction
For example, it is more efficient to write the status of 16 or 32 relays with one command (0x0F write multiple coils) than to write each one individually.
activate the checkbox little endian
-
Hi radar17892,
all set, the point is that we need somewhere define on which Marker Word to assign. This is done with MU-Modbus RTU acyclic request. If I set all of this parameters I will have on marker area assignment all 32 markers related to selected MW colored with green (Read). If I want to have Read/write is in yellow. To have the writ function must be orange.
When I upload program with this configuration I will have few seconds before Modbus RTU goes in fault. To reset the fault I need to reupload a program or reboot the PLC.
I'm also sniffing the communication between Master and Slave but no data is transferred.
-
Moreover if Start dress is 0 it's impossible to upload the project. See attach