English Support - Hardware => easyRelais => Thema gestartet von: jugasz am Oktober 25, 2013, 11:39:01 Vormittag
-
Hello ,
i have a question i work with 2 821-DC-TCX connected with the NET it works perfect but i don't have anymore memory,so now i try to write a program in the second one but how can i use the same markers from the first on or how do i have to send it from one to another.
thanks for you reply,
Jurgen
-
You have to use the GT and PT functionblocks for that. And remember, If you are accessing outputs from the first one directly ( e.g. using 2Q1, 2Q2 and so on ), you cannot put a program on the second controller.
You have to use the GT and PT blocks for all the communication.
Greets,
Spellbreaker