Troubles using Darwin.
« am: September 07, 2010, 20:13:56 Nachmittag »
Hi to all!, i managed to make Darwin work with one element. But, unfortunetly when i try to add another element,  the net cant recognize this new element. If i deattach the old element, the net recongize the new element without problem. So, in conclution, the gateway cant recognize two elements at the same time...

Can anyone help me with this?

Thanks in advance...

Nicolas.

Offline ALU

  • Newbie
  • *
  • Beiträge: 8
Re: Troubles using Darwin.
« Antwort #1 am: September 15, 2010, 14:35:11 Nachmittag »
Hi nicool67,

your problem may be the connection to the plc. If your gateway is in operational mode or has been in operational mode it will reject any requests to rescan the swd-bus for new bus-members.
(Since the currently saved configuration on the swd-gateway is compatible with the configuration requested by the plc the rescan request is seen as an operating error.)
The safest way to rescan the swd-bus is to restart the swd-gateway without the plc being connected to it. Then start the rescan by pressing the “Config”-button for about 2 sec.

Regards

ALu

Offline nicool67

  • Jr. Member
  • **
  • Beiträge: 27
Re: Troubles using Darwin.
« Antwort #2 am: Dezember 02, 2010, 11:36:06 Vormittag »
It worked!, i believe youre rigth about the comunication cable.

If someone needs an example send me a message.

Thanks a lot!.