Hi there

Im looking for some Help! Does any one have an example for a pump change over circuit?

I have 2 pumps that i have to control.

(Pump Selection )

I1 = Pump 1 - Pump 2
I2 = Pump 2 - Pump1

If the overload or the flow switch failes(I4) it will select the next pump after a delay of 1min. When a reset button is pressed (I3) it wll change back over on to the lead pump that is selected via the switch (I1 or I2).

Regards

Tommy

Offline julian

  • Full Member
  • ***
  • Beiträge: 184
  • I love easy-Forum.net
Re: Pump Changeover
« Antwort #1 am: Februar 07, 2005, 20:58:49 Nachmittag »
Tommy,
see my attached example.Easy-Soft V 5.11pro.
I use two jumps.That works in conjunction with I01 and I02 like a program selector switch.
May be it can serve as a basic for your application.
Regards,
Julian

Offline tommyrush

  • Jr. Member
  • **
  • Beiträge: 28
  • I love easy-Forum.net!
Re: Pump Changeover
« Antwort #2 am: Februar 08, 2005, 19:53:19 Nachmittag »
Julian

Thanks for the application you sent, works very well. ;D