Hi
It's not so Easy. You use the analog inputs at the Easy 819 relais.
-First you have to send the analog values by PUT functionsbloc from Easy 819 into Easy-Net.
-Second you have to read them by GET functionsbloc into the MFD.
It means, you need a programm in the EASY (PUT) as well in the MFD (GET). If you could install the analog inputs direct at the MFD inputs, the programm would be much more simple.