Autor Thema: Change time on Timing Relay with input  (Gelesen 3749 mal)

Offline fentini

  • Newbie
  • *
  • Beiträge: 4
Change time on Timing Relay with input
« am: Februar 21, 2023, 11:56:36 Vormittag »
Hello,
I would like to change the time a timer runs according to a digital or analog input that I connect to my Eaton Easy E4.
There is this valve that is being opened by the eaton e4. But sometimes I want the valve to open longer/shorter. I thought I would buy a 0-10 V generator and then connect it to Input 5 of the relais so that I can increase/decrease the voltage on that input. Then on the software I change the I1 of the Timing Relais to "analog inputs/outputs and markers". But that is where I get stuck. Perhaps there are people who can help or maybe there is a topic on this which I have not found?

Thanks in advance.
Chris

Offline radar17892

  • Sr. Member
  • ****
  • Beiträge: 788
  • Think easy!
    • mollgruppe
Antw:Change time on Timing Relay with input
« Antwort #1 am: Februar 21, 2023, 13:26:36 Nachmittag »
Hi Chris,
is the LD below, that what you mean?
Note: a time change at the input while the timer is running has no effect. The input is only read at the start of the timer.

Regards Thomas
Weil Einfach einfach Einfach ist!

Offline fentini

  • Newbie
  • *
  • Beiträge: 4
Antw:Change time on Timing Relay with input
« Antwort #2 am: Februar 22, 2023, 12:40:40 Nachmittag »
Hi Chris,
is the LD below, that what you mean?
Note: a time change at the input while the timer is running has no effect. The input is only read at the start of the timer.

Regards Thomas

Oh wow, yes, thanks a lot!! You helped me a lot.
Happy with that!!!!!!!!!
Regards Chris