Autor Thema: Formula of PT filter in MFD-TAP13-PT-A  (Gelesen 39079 mal)

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #15 am: November 17, 2014, 10:27:07 Vormittag »
Hello Thomas

Do you think a symbol of PT1 filer in the Easy Project may be: PTO1/1, PT02/1
« Letzte Änderung: November 17, 2014, 10:31:02 Vormittag von Elka »

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #16 am: November 17, 2014, 10:39:22 Vormittag »
You may find a file in the attachment. A Polish automatic engeener told me that he cannot find any software filter in this project..

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #17 am: November 17, 2014, 10:40:27 Vormittag »
Here is another one..

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #18 am: November 17, 2014, 10:42:21 Vormittag »
..the third one:


Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #19 am: November 17, 2014, 10:43:44 Vormittag »
and the last one..

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #20 am: November 17, 2014, 10:48:20 Vormittag »
I have obtained such an e-mail from Eato:

"Dear Mrs. Elzbieta Wierzchowska,


please excuse my late reply. What exactly do you want? Read temperature
and record? This filter (low pass and PT1 behaviour) smoothes the analog
 input signals. This suppresses variations in the temperature sensor
values that are caused by high-frequency interference. Note: More
effective filtering, however, is provided by a hardware filter, which is
implemented by the A/D converter. You can set this hardware filter via
the Filter area.

The staggered use of hardware and software filters drastically increases
the recovery time. This should not, however, be greater than necessary,
otherwise the signals will be delayed more than is required by the
smoothing. (This is an excerpt from the Easysoft help!)"

They have not sent me any useful information so far.
Unfortunately my data seem not to switch a formula of the filter..




Offline radar17892

  • Sr. Member
  • ****
  • Beiträge: 788
  • Think easy!
    • mollgruppe
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #21 am: November 18, 2014, 12:07:00 Nachmittag »
Hi Elka,

I could see the code this morning. Without comments, it was difficult, but I understand it.
As your engineer said, there are no FT blocks in the program.
Unfortunately, I do not know the exact formula for the modul filter. If it does not tell EATON, one could only determine approximately with traces.
Some parameters of the filter I've marked you in the picture.
For a higher resolution of the sensor values, I would switch to 0.1 ° C. There are but then the program several parameters to change.
The filter can be set to 50ms sampling rate.

regards Thomas
Weil Einfach einfach Einfach ist!

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #22 am: November 18, 2014, 15:22:25 Nachmittag »
Hello Thomas,

thank you for your answear. We were trying to change scaling while switching off the filter, but our Giesen coffee roaster: GW15 have not wanted to  work after this change..

Today I was contacted by a Polish Eaton representative, mister Jacek Zarzycki who told me that  Eaton Central Office rapresented by  mister Roberto Ariosto considers parameters of lower pass-filters are "prioprietary" so they cannot be announced to anybody..

From the same Roberto Ariosto I recevied a month ago the following e - mail:

"Dear Mrs. Elzbieta Wierzchowska,

please excuse my late reply. What exactly do you want? Read temperature and record?
This filter (low pass and PT1 behaviour) smoothes the analog input signals. This
suppresses variations in the temperature sensor values that are caused by
high-frequency interference.
Note: More effective filtering, however, is provided by a hardware filter, which is
implemented by the A/D converter. You can set this hardware filter via the Filter
area.

The staggered use of hardware and software filters drastically increases the
recovery time. This should not, however, be greater than necessary, otherwise the
signals will be delayed more than is required by the smoothing.
(This is an excerpt from the Easysoft help!)


Should you have any further questions, please do not hesitate
to contact us.


With best regards
Avec de sincères salutations / Con cordiales saludos


Roberto Ariosto
Applikations-& Produktsupport Automation
Produktsupport Safety Technology

************************************************************
Eaton Industries GmbH
Electrical Sector / Industrial Automation Business
IAB-MTS / Applikations- & Produktsupport
Hein-Moeller-Str. 7-11
D-53115 Bonn"

Today a  Polish represnative of the same company told me that filtering "improve precision of measurments"..

 

Offline radar17892

  • Sr. Member
  • ****
  • Beiträge: 788
  • Think easy!
    • mollgruppe
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #23 am: November 20, 2014, 12:02:59 Nachmittag »
Hi Elka,

I wrote, if you change the resolution, you must also change the program. The machine could not work like that.
I send you a new program file with the changes, so it works.
The changes are indicated in the images.
My idea was to determine the temperature in high resolution read by MD30 / 31 for the SCADA and the values in 1 ° C resolution output to MD10 / 11 on the old program.
Please change the SCADA system to the read access of MD24 (it`s ° C / ° F) -> MD30 (only 0.1 ° C) and MD25 -> MD31 to.
I hope your measurement process is better!

Thomas

PS: I could not install the sensor offset for a PT100 calibration in the program because of insufficient memory.
Weil Einfach einfach Einfach ist!

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #24 am: November 20, 2014, 12:13:27 Nachmittag »
Dear Thomas,

You are so nice and helpful! Thank you so much!
Elisabeth

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #25 am: November 20, 2014, 17:10:33 Nachmittag »
After thinking and calculation I was able to give to a student who is writing a software for us the following instruction to estimate my roasting profiles registered with PT1 filter ON for T-bean..since time 30s after charge:

Ror=Rate of rise of T-bean (calculated by 30s)
T-bean_new=estimated "right", non smoothed T-bean
T-bean="old smoothed temperature)

T_bean_new (30s)=T-bean-2/3 Ror
T_bean_new (60s)=T_bean-Ror
T_bean_new (100s/1min.40s)=T_bean+Ror

t100s=Phidget "real" minimum for our profiles

T-bean_new (140s /2 min 20s)=T_bean+1/2 Ror
T_bean_new (150s /2 min 30s)=T_bean (!)
T_bean_new (165s /2 min 45 s)=T_bean+6C

6C is a half of the BT amplitude which was "allowed" by PT1 filter during auto-mode oscillations.

T_bean+new (180s /3 min)=T_bean + 6C
T_bean_new (205s /3 min 15 s)=T_bean + 3*Ror
T_bean_new (210s /3 min 30s)=T_bean+2*Ror

after..to the the end of the roasting curve:
T-bean_new(n)=T_bean+2*Ror..

We are still looking for a right formula to estimate our past charging temperatures.
It is possible to say more about formula of the  PT1 filter from my calculations?

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #26 am: November 21, 2014, 12:56:33 Nachmittag »
Hi Thomas,
Somebody from the Polish Forum Elektroda wrote that for a graphic rapresentation of PT1 filter this page may be very useful: 

http://en.wikipedia.org/wiki/Bode_plot

What do you think about it?
All the best,
Elisabeth

Offline radar17892

  • Sr. Member
  • ****
  • Beiträge: 788
  • Think easy!
    • mollgruppe
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #27 am: November 27, 2014, 21:36:03 Nachmittag »
Hi Elka,

I tried to replicate the heating curve of the roaster mathematically.
In the program, a two-position controller works.
The diagram is not entirely correct, but it should show about the heating curve.
(1-e^(-t/T))repesents a PT1 delay.

If you want to have an exact curve of the filter, you need the sensor to the hardware simulate and record a step response.

Thomas
« Letzte Änderung: November 27, 2014, 21:53:47 Nachmittag von radar17892 »
Weil Einfach einfach Einfach ist!

Offline Elka

  • Jr. Member
  • **
  • Beiträge: 24
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #28 am: November 28, 2014, 08:21:15 Vormittag »
Dear Thomas,

you are incredible! Thank you so much!!!

Elisabeth

Offline radar17892

  • Sr. Member
  • ****
  • Beiträge: 788
  • Think easy!
    • mollgruppe
Re:Formula of PT filter in MFD-TAP13-PT-A
« Antwort #29 am: November 28, 2014, 11:56:30 Vormittag »
Hi Elka,
can you send me a set of measurement data of the step response?
Unfortunately I have no MFD hardware to make it yourself.

please proceed as follows:
To Build a circuit with changeover switch by an electrician.

0 --- --- R100,00 \                                    =0°C
     |                    switch --- 0
     | _R175,84_ /                                     =200°C

The resistors have to be as exact as possible.
(possibly from potentiometers build)

terminal of this circuit instead of the PT100 T1.
Set PT filter ON.
Start easysoft in online mode with oscilloscope
Create the record of the MD30 and turn the switch to 175 Ohm.
stop the measurement when the value is stable. It should not take longer than a minute.

Now you have a step response of the filter only. With dataset can derive a formula from.

Note: Do not start the roaster, only the PLC must be in RUN mode!
Weil Einfach einfach Einfach ist!