Analogue Input
« am: März 16, 2021, 10:40:30 Vormittag »
I have wired up a 4-20mA transducer to an easy e4 with an analogue module. I have checked the cable is ok but for some reason the scaled figures for the input which i have done in meters in a tank jump around quite a bit. Is there anything i can do about this. Cheers

Offline Frohnius

  • Jr. Member
  • **
  • Beiträge: 40
Antw:Analogue Input
« Antwort #1 am: März 16, 2021, 12:20:29 Nachmittag »
hi,
[/size]which scale did you set up for your analog in ?
[/size]perhaps you should set your analog in 4-20mA to 4000-20000 ...
[/size]did you activate in the input setup to smooth the input 0-16 measured values


[/size]set your LS to output mm ...
[/size]and then calculate to meters
[/size]


Offline srd

  • Jr. Member
  • **
  • Beiträge: 95
Antw:Analogue Input
« Antwort #2 am: März 16, 2021, 16:16:06 Nachmittag »
Cheers for that i will set it and try.

Offline srd

  • Jr. Member
  • **
  • Beiträge: 95
Antw:Analogue Input
« Antwort #3 am: März 16, 2021, 16:17:22 Nachmittag »
How many ms would you recommend

Offline weiss_nix

  • Sr. Member
  • ****
  • Beiträge: 599
  • it has to be easy, it's a easy!
Antw:Analogue Input
« Antwort #4 am: März 17, 2021, 07:37:29 Vormittag »
Hello srd,
the issue with the unstable measured values ​​has often been the topic here in the forum. Most of the time it was a grounding problem.

regards