Autor Thema: transducer failure  (Gelesen 231 mal)

Offline srd

  • Full Member
  • ***
  • Beiträge: 142
transducer failure
« am: April 21, 2026, 07:43:25 Vormittag »
we are using a 4-20mA transducer to open / close a mains water valve, is there a way of monitoring the transducer as we have had them fail midrange and the valve stayed open and over filled the tank, we have put in a high level float as a back up to everything off in case it happens again.

Offline Konni66

  • Global Moderator
  • Full Member
  • *****
  • Beiträge: 312
  • Keine Panik!
    • Eaton Trainingscenter Bonn
Antw:transducer failure
« Antwort #1 am: Gestern um 16:08:15 »
Hello srd,
you can monitor transducer value through a comperator.
If the transducer fails since error in its power supply or broken wire there're measuring values below 412 increments -> close valve immidiatly.
If valve is open check every n seconds if filling level is moving. If not close valve.
Greetz Konni
Die Programmierbeispiele sind zu Schulungszwecken gedacht. Trotz sorgfältiger Erstellung und Funktionsprüfung können Fehler nicht ausgeschlossen werden. Daher erfolgt die Verwendung der Programmteile in eigener Verantwortung.