Autor Thema: Value Scaling Issue  (Gelesen 707 mal)

Offline Gayathri L

  • Newbie
  • *
  • Beiträge: 1
Value Scaling Issue
« am: Januar 27, 2024, 12:26:54 Nachmittag »
Hi,

I'm working on Eaton EASY-E4-DC-12TC1P and EasySoft 7 V7.4.1.

I have a issue when I'm using LS-Value Scaling component.
Please find the attached pdf of LD program where Network 1 to Network 10 work perfectly fine before adding Network 11. Once Network 11 (LS-Vaue Scale) is added, the Cycle_Started marker is failing to set and is giving unexpected results.

Please help me out with this issue as I'm new to Eaton and EasySoft.


Offline Juergen

  • easy god
  • *****
  • Beiträge: 1950
  • Jürgen
Antw:Value Scaling Issue
« Antwort #1 am: Januar 27, 2024, 19:58:04 Nachmittag »
Hallo,

Hello,

you use bit flags M 1,2,3,4 ... and in network 11 the MW 1.
These influence each other.

Use a different MW on network 11
See image


du verwendest Bit Merker M 1,2,3,4 ... und in Netzwerk 11 das MW 1.
Das beeinflusst sich gegenseitig.

Verwende in Netzwerk 11 ein anderes MW
« Letzte Änderung: Januar 27, 2024, 20:49:51 Nachmittag von Juergen »
Mit freundlichem Gruß Juergen


Alle Programme sind nur Beispiele und Selber zu Testen.
Geprüft wurde nur in der Simulation der Software oder mit Simulator am Schreibtisch. Die Beispiele sind mit Sicherheitsschaltungen zu ergänzen.